![](https://pdfstore-manualsonline.prod.a.ki/pdfasset/a/d7/ad722da2-d369-4efc-b7c2-1152a01c2f4c/ad722da2-d369-4efc-b7c2-1152a01c2f4c-bg15.png)
T874 MULTISTAGE THERMOSTATS AND Q674 SUBBASES
21 60-2485—8
OPERATION
Heat Anticipation/Cool Anticipation
When controllin
a heatin
unit with a thermostat, the
temperature does not remain exactl
at the thermostat
setpoint, but varies within a certain temperature ran
e. Heat
anticipation is added to the thermostat to reduce this ran
e.
The anticipator is a small resistive heater in the thermostat
that heats when the s
stem is on
heat mode
or off
cool
mode
. The heat produced b
the anticipator raises the
internal bimetal temperature sli
htl
faster than the
surroundin
room temperature. The thermostat
anticipates
the need to shut off the heatin
s
stem sooner than it would if
affected b
room temperature onl
.
There are two t
pes of heat anticipation, ad
ustable and fixed.
Ad
ustable anticipation is also called
current anticipation
. See
Fi
. 26. The heater is in series with the mercur
switch and
heatin
primar
. The pointer is ad
usted to match the current
draw of the primar
control, and the correct amount of heat is
added for proper c
cle rates.
Fig. 26. Adjustable anticipation heater in series with load.
Fixed anticipation is also called
voltage anticipation
. See
Fi
. 27. The heater is in parallel with the primar
control and is
not affected b
the current draw of the primar
. It establishes
the proper c
cle rate for an
application.
Fig. 27. Fixed anticipation heater in parallel with load.
Heat anticipators add heat durin
the call for heat. Coolin
anticipators are activated while the air conditioner is off. See
Fi
. 28. This heater makes the thermostat think it is warmer than
it reall
is, and brin
s it on sooner than the bimetal alone would.
Fig. 28. Internal cooling anticipation schematic.
Interstage Differential
The mercur
switch of each sta
e of heat makes at a sli
htl
different temperature; that is, the mercur
makes the contacts
of the first sta
e bulb at one temperature, and the second
sta
e bulb at another temperature. The difference between
these two temperatures is the
interstage differential
.
Intersta
e differential is the difference between the two make
points when the bulbs are controlled b
the heatin
of the
bimetal and the action of the heat anticipator. The intersta
e
differential is 1.9°F
1°C
between the sta
es of heatin
or the
sta
es of coolin
for most models.
Mechanical differential is the difference between the make
and break points of each switch. The mechanical differential
for the T874 is 1°F
0.6°C
between the sta
es of heatin
or
between the sta
es of coolin
for most models.
Droop
The addition of anticipator heat to the bimetal causes a control
factor called
droop
.
As the weather
rows colder, the heatin
appliance must
operate lon
er and more fre
uentl
. More heat must be added
to the bimetal. The bimetal now thinks it is warmer than it
reall
is, and actual room temperature is controlled at a lower
temperature than the setpoint indicates. At 100 percent heat
load, this droop can be si
nificant.
The C815A Outdoor Reset Thermistor is used in heat pump
s
stems to minimize droop. Without some method of
counterin
this situation, the occupant could notice the
temperature offset.
Outdoor Reset
Some T874/Q674 models are intended for use with the
C815A Outdoor Thermistor. The outdoor thermistor provides
si
nificantl
improved thermostat performance when
compared to conventional multista
e thermostats. The C815A
is usuall
located in the heat pump condensin
unit outdoors.
FALL
L1
(HOT)
L2
M5823
STAGE 1 HEAT RELAY
H1 ANTICIPATOR
H1
FALL
L1
(HOT)
L2
M5824
STAGE 1
HEAT RELAY
H1 ANTICIPATOR
H1
RISE
L1
(HOT)
L2
M5825
STAGE 1
COOL RELAY
C1 ANTICIPATOR
C1